Biggest issue with gas work is not the permit or the inspection, it’s the pressure test. You have to shut off all appliances, using shutoff valves located before the appliances, hook up the gauge to the line, leave it pressurized for 24 hours (with air!), and have the inspector verify. It’s a royal pain in the neck for the homeowner.
You may be able to talk the building department into doing the inspection without the pressure test.
Were it me, I would just do it without the permit.
October 1, 2010 at 6:39 PM #611759FearfulParticipantBiggest issue with gas work is not the permit or the inspection, it’s the pressure test. You have to shut off all appliances, using shutoff valves located before the appliances, hook up the gauge to the line, leave it pressurized for 24 hours (with air!), and have the inspector verify. It’s a royal pain in the neck for the homeowner.
You may be able to talk the building department into doing the inspection without the pressure test.
Were it me, I would just do it without the permit.
October 1, 2010 at 6:39 PM #612307FearfulParticipantBiggest issue with gas work is not the permit or the inspection, it’s the pressure test. You have to shut off all appliances, using shutoff valves located before the appliances, hook up the gauge to the line, leave it pressurized for 24 hours (with air!), and have the inspector verify. It’s a royal pain in the neck for the homeowner.
You may be able to talk the building department into doing the inspection without the pressure test.
Were it me, I would just do it without the permit.
October 1, 2010 at 6:39 PM #612423FearfulParticipantBiggest issue with gas work is not the permit or the inspection, it’s the pressure test. You have to shut off all appliances, using shutoff valves located before the appliances, hook up the gauge to the line, leave it pressurized for 24 hours (with air!), and have the inspector verify. It’s a royal pain in the neck for the homeowner.
You may be able to talk the building department into doing the inspection without the pressure test.
Were it me, I would just do it without the permit.
October 1, 2010 at 6:39 PM #612735FearfulParticipantBiggest issue with gas work is not the permit or the inspection, it’s the pressure test. You have to shut off all appliances, using shutoff valves located before the appliances, hook up the gauge to the line, leave it pressurized for 24 hours (with air!), and have the inspector verify. It’s a royal pain in the neck for the homeowner.
You may be able to talk the building department into doing the inspection without the pressure test.
Were it me, I would just do it without the permit.
October 2, 2010 at 1:36 PM #611791AnonymousGuestPermit or no permit make sure it is installed and tested per code, preferably by a licensed, bonded, insured plumber. The liability and potential for San Bruno type excitement is just to great with gas sytems.
As stated before the intent of the code and the administrative authority, (City of San Diego?), requires an inspection before use. Section 1204.1 – 2007 CPC / UPC.
In low pressure residential gas piping,(under 1/2#psi),the code requires testing at a minimum of 10 minutes and maximum of 24 hours at 1-1/2 times the working pressure or minimum 3#psi. The reality is in most cases if everything is installed correctly and ready under test you will spend more time waiting for the inspector than the actual on site inspection. The inspector has the discretion, following the intent of the code, to determine the length of the inspection.
If you go the inspetion route make sure all of the related plumbing is up to code for obvious reasons.
Using the December 09 permit worksheet I calculate a total permit cost of $177.00 for the 1 gas outlet. Keep in mind if other plumbing work is involved the inspector may want documentation, which could mean additional permit fees. The fee schedule and permit apps are on line.
October 2, 2010 at 1:36 PM #611878AnonymousGuestPermit or no permit make sure it is installed and tested per code, preferably by a licensed, bonded, insured plumber. The liability and potential for San Bruno type excitement is just to great with gas sytems.
As stated before the intent of the code and the administrative authority, (City of San Diego?), requires an inspection before use. Section 1204.1 – 2007 CPC / UPC.
In low pressure residential gas piping,(under 1/2#psi),the code requires testing at a minimum of 10 minutes and maximum of 24 hours at 1-1/2 times the working pressure or minimum 3#psi. The reality is in most cases if everything is installed correctly and ready under test you will spend more time waiting for the inspector than the actual on site inspection. The inspector has the discretion, following the intent of the code, to determine the length of the inspection.
If you go the inspetion route make sure all of the related plumbing is up to code for obvious reasons.
Using the December 09 permit worksheet I calculate a total permit cost of $177.00 for the 1 gas outlet. Keep in mind if other plumbing work is involved the inspector may want documentation, which could mean additional permit fees. The fee schedule and permit apps are on line.
October 2, 2010 at 1:36 PM #612426AnonymousGuestPermit or no permit make sure it is installed and tested per code, preferably by a licensed, bonded, insured plumber. The liability and potential for San Bruno type excitement is just to great with gas sytems.
As stated before the intent of the code and the administrative authority, (City of San Diego?), requires an inspection before use. Section 1204.1 – 2007 CPC / UPC.
In low pressure residential gas piping,(under 1/2#psi),the code requires testing at a minimum of 10 minutes and maximum of 24 hours at 1-1/2 times the working pressure or minimum 3#psi. The reality is in most cases if everything is installed correctly and ready under test you will spend more time waiting for the inspector than the actual on site inspection. The inspector has the discretion, following the intent of the code, to determine the length of the inspection.
If you go the inspetion route make sure all of the related plumbing is up to code for obvious reasons.
Using the December 09 permit worksheet I calculate a total permit cost of $177.00 for the 1 gas outlet. Keep in mind if other plumbing work is involved the inspector may want documentation, which could mean additional permit fees. The fee schedule and permit apps are on line.
October 2, 2010 at 1:36 PM #612542AnonymousGuestPermit or no permit make sure it is installed and tested per code, preferably by a licensed, bonded, insured plumber. The liability and potential for San Bruno type excitement is just to great with gas sytems.
As stated before the intent of the code and the administrative authority, (City of San Diego?), requires an inspection before use. Section 1204.1 – 2007 CPC / UPC.
In low pressure residential gas piping,(under 1/2#psi),the code requires testing at a minimum of 10 minutes and maximum of 24 hours at 1-1/2 times the working pressure or minimum 3#psi. The reality is in most cases if everything is installed correctly and ready under test you will spend more time waiting for the inspector than the actual on site inspection. The inspector has the discretion, following the intent of the code, to determine the length of the inspection.
If you go the inspetion route make sure all of the related plumbing is up to code for obvious reasons.
Using the December 09 permit worksheet I calculate a total permit cost of $177.00 for the 1 gas outlet. Keep in mind if other plumbing work is involved the inspector may want documentation, which could mean additional permit fees. The fee schedule and permit apps are on line.
October 2, 2010 at 1:36 PM #612856AnonymousGuestPermit or no permit make sure it is installed and tested per code, preferably by a licensed, bonded, insured plumber. The liability and potential for San Bruno type excitement is just to great with gas sytems.
As stated before the intent of the code and the administrative authority, (City of San Diego?), requires an inspection before use. Section 1204.1 – 2007 CPC / UPC.
In low pressure residential gas piping,(under 1/2#psi),the code requires testing at a minimum of 10 minutes and maximum of 24 hours at 1-1/2 times the working pressure or minimum 3#psi. The reality is in most cases if everything is installed correctly and ready under test you will spend more time waiting for the inspector than the actual on site inspection. The inspector has the discretion, following the intent of the code, to determine the length of the inspection.
If you go the inspetion route make sure all of the related plumbing is up to code for obvious reasons.
Using the December 09 permit worksheet I calculate a total permit cost of $177.00 for the 1 gas outlet. Keep in mind if other plumbing work is involved the inspector may want documentation, which could mean additional permit fees. The fee schedule and permit apps are on line.
October 2, 2010 at 5:34 PM #611855ryphoenixParticipantWow thanks BC, you really know your stuff!
I just bought the house so I have no idea if other stuff are up to code, though most if not everything in this house seems to have been done by the code.
I think at this time I’m gonna skip the permit unless someone else convinces me otherwise.
October 2, 2010 at 5:34 PM #611943ryphoenixParticipantWow thanks BC, you really know your stuff!
I just bought the house so I have no idea if other stuff are up to code, though most if not everything in this house seems to have been done by the code.
I think at this time I’m gonna skip the permit unless someone else convinces me otherwise.
October 2, 2010 at 5:34 PM #612490ryphoenixParticipantWow thanks BC, you really know your stuff!
I just bought the house so I have no idea if other stuff are up to code, though most if not everything in this house seems to have been done by the code.
I think at this time I’m gonna skip the permit unless someone else convinces me otherwise.
October 2, 2010 at 5:34 PM #612605ryphoenixParticipantWow thanks BC, you really know your stuff!
I just bought the house so I have no idea if other stuff are up to code, though most if not everything in this house seems to have been done by the code.
I think at this time I’m gonna skip the permit unless someone else convinces me otherwise.
-